I have a geist phantom rg, which has an intermittent fault. This is that it sometimes trips the site 240v supply (this has happened on more than one site)

I have had my supply cable and van checked but no fault found.

Has anyone else had this problem with the same motorhome ? *-)

Link to comment
Share on other sites

A favourite irem for causing trip outs are electric kettles. Also any thing with a water heater in it (on board water heater?).

 

If the wiring checks out you have to either test every one of the appliances to find the fault (difficult if it's intermittant) or just note what was "on" when the trip operates, and do it by elimination.

 

The on board trip should aslo trip out but it depends on some technical specs. They might actually not trip, the site trip being faster or more sensitive.

 

A spiders nest in a socket was the cause in one case I know of!

 

Is any damp getting into the back of the input socket? The lead plugs/sockets are not waterproof, water will get in at times, wrap them in a polythene bag, it helps.

 

H

Link to comment
Share on other sites

Hi, Thank's for the info' I can confirm that the prob' is not caused by drawing too much power, and the input socket is dry.

The spiders nest is an interesting one, we have spiders, they keep the flies etc' down, I have arranged a PAT test to be done so that may disturb a few spiders.

I have also had the prob' using another cable.

 

 

 

Link to comment
Share on other sites

Hi again, I forgot to say that the electrician who will be doing the p A T Test says he will not be able to test anything which has a P c b in it. This I am told will include the fridge and the heating unit.
Link to comment
Share on other sites

jim1 - 2012-10-25 5:52 PM

 

Hi again, I forgot to say that the electrician who will be doing the p A T Test says he will not be able to test anything which has a P c b in it. This I am told will include the fridge and the heating unit.

 

He ain't no electrician as he should no how to do it

Link to comment
Share on other sites

Guest JudgeMental

I would guess the heater, Truma? there will be a mains connection box near unit, disconnect and try again. Presumably it does the same on 230V pluged in at home as on a campsite?

 

Dont sound like a spark to me.. why a PAT test? insulation/continuity test more like....

Link to comment
Share on other sites

Any Tom, Dick or Harry, who has had a very basic tutorial for the equipment can perform PAT testing, so does not necessarily have to be a qualified Electrician. (unless things have changed very recently).

 

Get a qualified Electrician or AutoElectrician to check this out.

Link to comment
Share on other sites

I would be trying to eliminate appliance one by one. For example run the fridge on gas and see if you still get a trip out. Ditto the space heater etc.

 

PAT or Portable Appliance Testing is a very broad term. The most basic of which is a visual inspection. This just covers a knowledgeable person looking at the cables and leads and plugs. More advanced checks include earth leakage and continuity testing etc.

If you are paying for a PAT establish exactly what is being checked.

Link to comment
Share on other sites

Hello all who replied to my query.

The problem I had was eventually traced to :- an airflow duct had come out of one of the heater / boiler outlets, the back one.

The hot air was blowing into a space where the 240v wiring / consumer unit is, as the heater got hotter and thus the wiring, this then degraded the insulation properties of the wiring causing an eventual partial failure which resulted in a trip out.

 

Thanks to you all who tried to help. :->

Link to comment
Share on other sites

jim1 - 2012-10-30 4:04 PM

 

Hello all who replied to my query.

The problem I had was eventually traced to :- an airflow duct had come out of one of the heater / boiler outlets, the back one.

The hot air was blowing into a space where the 240v wiring / consumer unit is, as the heater got hotter and thus the wiring, this then degraded the insulation properties of the wiring causing an eventual partial failure which resulted in a trip out.

 

Thanks to you all who tried to help. :->

Well done! Good job you got that sorted, as the potential for a fire from the wiring was there. Certainly wasn't the most obvious fault. Hope it wasn't too costly!