It is VITAL that the inverter and EHU are not powering the 240v system at the same time.

The best way to avoid that is auto selection of source ie when EHU is connected the inverter is automatically disconnected.

To answer your question, without knowing how your electrics, 12v and 240v are wired, it is impossible to say if battery isolator needs to be switched off.  But relying on having to remember to throw the switch is unsafe.  

Link to comment
Share on other sites

I am no electrician but following the advice above, I would suggest that a 3 pole, 2 way, centre off, 240 volt switch is required. The two feeds in are the 240 v mains supply and the other being the inverter 240 output.  The out from the switch would feed the mhome 240 volt circuit.

I can foresee problems trying to sort out the 240 Volt to 12 volt circuits.  

so maybe just consider the inverter 240 supply as being on separate sockets.